I got an email from a friend, more of them are finding out I hang out here and would rather have me ask a question for them, shy I guess.
Here is the email.
Any ideas?, you have all the info I was given.
Thanks Bob
[ March 29, 2004, 07:35 PM: Message edited by: iwire ]
Here is the email.
The no neutral amps but amps on the GEC make me think there is grounding bonding issues, but the breaker not holding I have no idea on.I have two 225 kva 480 - 120/208 GE transformers at XXXXXX.
The first has a core temp of 140 c. Very lightly loaded.
Primary
"A" 9.3 amps 23.2 %Thd
"B" 7.29 amps 29.3 %Thd
"C" 11.9 amps 28 % Thd
Secondary
"A" 13.9 amps 6.4 %Thd
"B" 15.45 amps 18.2 % Thd
"C" 7.95 amps 10.9 % Thd
No neutral amps but 8.76 amps 7.4 % Thd on the grounding electrode conductor.
Does this prim to secd ratio cause the core to heat up more?
Or is my core bad?
This is a new K Rated trans.
The second trans is right next to it.
Core temp 108 c
Primary
"A" 23.46,
"B" 22.89,
"C" 20.01
Secondary
"A" 61.78,
"B" 86.6,
"C" 54.70.
This ratio seems more realistic for 480 - 120/208. No neutral amps but 7.4 amps to grounding electrode conductor.
What do you think or can one of your friends help.
This came up because the GE 400 amp breaker feeding trans would not hold.
Any ideas?, you have all the info I was given.
Thanks Bob