Hello,
I was hoping to find some help troubleshooting a transformer problem...
We have a typical 600V-120/208V delta-wye transformer that is providing some problems. The problem was first noticed when several flourescent lights went out due to low voltage.
I went out and did some measurements at the suppy transformer and found that the phase to neutral voltage was low, only on B phase (98V compared to 123V on A and C phase). There was no neutral to ground voltage found (showed 293mV). The neutral wire had a current of 55.3 A.
Using a little Trig I was able to find that the B phase voltage is out of phase by 137? with the A phase and 103? with C phase instead of the 120? that it should be.
If anyone has any idea how I could go about troubleshooting this problem please let me know.
The load side of the transformer is feeding several 3 phase panels that go on to feed a variety of equipment including small pumps, fans, lighting, and heating.
I was hoping to find some help troubleshooting a transformer problem...
We have a typical 600V-120/208V delta-wye transformer that is providing some problems. The problem was first noticed when several flourescent lights went out due to low voltage.
I went out and did some measurements at the suppy transformer and found that the phase to neutral voltage was low, only on B phase (98V compared to 123V on A and C phase). There was no neutral to ground voltage found (showed 293mV). The neutral wire had a current of 55.3 A.
Using a little Trig I was able to find that the B phase voltage is out of phase by 137? with the A phase and 103? with C phase instead of the 120? that it should be.
If anyone has any idea how I could go about troubleshooting this problem please let me know.
The load side of the transformer is feeding several 3 phase panels that go on to feed a variety of equipment including small pumps, fans, lighting, and heating.