WHAT WOULD BE THE RESULTS OF A 3-PHASE DELTA-WYE 30 KVA X-FMR
480 x 208/120 4-WIRE. IF IT WAS LABELED AT THE FACTORY INCORECTLY SUCH AS A 60 CYCLE
BUT IT WAS REALLY A 50 OR 25CYCLE UNIT.! WE ARE HAVING A PROBLEM
WITH POPING THE POWER SUPPLY ON 4 DESKTOP COMPUTERS. WE HAVE
CHECKED ALL GROUNDING & NEUT. CONNECTIONS. TAPS, WINDING CONNECTIONS, ALL BRANCH CIRCUIT CONNECTIONS FROM THE PANEL TO
THE OUTLETS, ALL VOLTAGES ARE AT 119 TO 121 VOLTS, WE REGROUNDED
THE MAIN PANEL, XFMR, & BUILDING STEEL, MEASURED FROM OTHER POSS-
IABLE GROUND AND OR REFERENCE POINTS AND FOUND NO MAJOR PROBLEM,
WE HAVE FOUND NO FLOATING NEUTRALS, OR GROUNDS WITH VOLTAGE DIFFERENTIAL ON THEM.
480 x 208/120 4-WIRE. IF IT WAS LABELED AT THE FACTORY INCORECTLY SUCH AS A 60 CYCLE
BUT IT WAS REALLY A 50 OR 25CYCLE UNIT.! WE ARE HAVING A PROBLEM
WITH POPING THE POWER SUPPLY ON 4 DESKTOP COMPUTERS. WE HAVE
CHECKED ALL GROUNDING & NEUT. CONNECTIONS. TAPS, WINDING CONNECTIONS, ALL BRANCH CIRCUIT CONNECTIONS FROM THE PANEL TO
THE OUTLETS, ALL VOLTAGES ARE AT 119 TO 121 VOLTS, WE REGROUNDED
THE MAIN PANEL, XFMR, & BUILDING STEEL, MEASURED FROM OTHER POSS-
IABLE GROUND AND OR REFERENCE POINTS AND FOUND NO MAJOR PROBLEM,
WE HAVE FOUND NO FLOATING NEUTRALS, OR GROUNDS WITH VOLTAGE DIFFERENTIAL ON THEM.