First time in this scenario. I have a pre-wired 25kva, 3~ 208 delta to (multi-tap) 400v 3~ Y transformer with multiple breakers and primary switch/disconnect incorporated into it. The machine that it is feeding is 3~ 4wire, 400v at 5.5 (KW) rated at 13 amps.
Originally the trnsfrmr was designed to handle more than one machine. We are now using one trnsfrmr per machine for redundancy reasons and I would like to protect the trnsfrmr correctly.
Do I still have to protect the trnsfrmr for its nameplate or can I protect it for the nameplate of the machine ( or load being served) at 30 amps from the panel?