Hey guys,
I have a 0.5 kVA, 480-240V single-phase transformer that's being protected by a 2 AT fuse on the primary. Is this a transformer protection issue? According to Table 450.3(B), the maximum rating of the OCPD on the primary is 167% of the primary current (currents less than 9 amperes).
My calculations:
Ip = 500VA / 480V = 1.04167A
1.04167A * 1.67 = 1.73958A, which is less than 2A (fuse rating)
Question remains: is this a transformer protection issue, or is there some kind of "round-up rule" for XFMRs?
I have a 0.5 kVA, 480-240V single-phase transformer that's being protected by a 2 AT fuse on the primary. Is this a transformer protection issue? According to Table 450.3(B), the maximum rating of the OCPD on the primary is 167% of the primary current (currents less than 9 amperes).
My calculations:
Ip = 500VA / 480V = 1.04167A
1.04167A * 1.67 = 1.73958A, which is less than 2A (fuse rating)
Question remains: is this a transformer protection issue, or is there some kind of "round-up rule" for XFMRs?