Re: Transformer Protection
Most if not all of the PM Transformer are protected with 1) Bayonet fuse and Partial Range Current limiting (PRCL)fuse connected in series with the Bay fuse.
I'm not sure that I agree with that, but this type of protection is common for three phase padmounted transformers owned by utilities.
If you aren't governed by the NEC, you would obtain a threshold of damage curve for the transformer. You would use the bayonet fuse to protect the thermal part of the curve, and the current limiting fuse to protect the magnetic portion if you could. The CL fuse would also be coordinated to prevent tank rupture.
If you are governed by the NEC, refer to Article 450.
Jim T