Please help me to clarify my understanding
Supply voltage is 240 Delta
Load is 208V rated at 45KVA
Need a 45KVA transformer
I size the secondary conductors and the secondary fuses as follows:
125A x 1.25 = 156 A
Secondary conductors 2/0
Secondary fused disconnect with 150A fuses. Maximum fuse FLA 125 x 175% = 218A
Primary side:
Supply voltage 240
45000/240/1.732 = 108A
Primary conductors
108 x 1.25 = 135 A = 1/0
Primary side OCPD 150A circuit breaker
Am I missing anything?
Is my understanding correct?
TIA.