I have an interesting problem / question. I can't find this exact scenario in another post....so I thought I would try a new post.
I am retro-fitting an installation, that was installed under the 1993 NEC.
The basics are:
A single transformer rated 13.8kv primary / 575 VAC secondary @ 2200 amps. This transformer has a primary fused disconnect and no direct secondary protection (the secondary has CTs, that trip a 13.8kv Circuit breaker that feeds this, and other transformers).
After the CTs, on the secondary side that transformer has two parallel feeds, each feeding a 2500 amp breaker (each breaker feeds a large DC drive).
My questions:
1. Using the 2005 NEC can I still use only these CTs for secndary protection (the transformer sits outside, and feeds the drives inside about 50' away).
2. Can I replace the 2500 Amp circuit breakers with 2000 Amp breakers OR do both breakers need to be able to take and interrupt the full 2200 amps?
Thanks,
I am retro-fitting an installation, that was installed under the 1993 NEC.
The basics are:
A single transformer rated 13.8kv primary / 575 VAC secondary @ 2200 amps. This transformer has a primary fused disconnect and no direct secondary protection (the secondary has CTs, that trip a 13.8kv Circuit breaker that feeds this, and other transformers).
After the CTs, on the secondary side that transformer has two parallel feeds, each feeding a 2500 amp breaker (each breaker feeds a large DC drive).
My questions:
1. Using the 2005 NEC can I still use only these CTs for secndary protection (the transformer sits outside, and feeds the drives inside about 50' away).
2. Can I replace the 2500 Amp circuit breakers with 2000 Amp breakers OR do both breakers need to be able to take and interrupt the full 2200 amps?
Thanks,