Is this misleading for transformer overcurrent protection:
NEC section 450.3 refers you to the transformer overcurrent protection tables 450.3(A) & 450.3(B). The tables list different overcurrent protection percentages based on primary only protection or a combination of primary and secondary protection. No where in these tables (in the title or in the key notes) does it say that secondary protection is required for all transformers (except 1-phase, 2-wire transformers and 3-phase delta-delta, 3-wire transformers per section 240.4 (F)).
I came across section 240.4 (F) just recently. But I thought it was misleading to go to the transformer tables in 450.3 and think that the information in these tables was enough to make a decision on whether or not to provide primary only protection simply following the percentages listed in the tables.
Example: 50A load, 3-phase, 4-wire wye transformer. Go to table 450.3(B) and select 125% primary only protection with secondary protection not required. But it IS required according to section 240.4 (F).
Shouldn't there be a note here in these tables stating this? Am I overlooking something?
NEC section 450.3 refers you to the transformer overcurrent protection tables 450.3(A) & 450.3(B). The tables list different overcurrent protection percentages based on primary only protection or a combination of primary and secondary protection. No where in these tables (in the title or in the key notes) does it say that secondary protection is required for all transformers (except 1-phase, 2-wire transformers and 3-phase delta-delta, 3-wire transformers per section 240.4 (F)).
I came across section 240.4 (F) just recently. But I thought it was misleading to go to the transformer tables in 450.3 and think that the information in these tables was enough to make a decision on whether or not to provide primary only protection simply following the percentages listed in the tables.
Example: 50A load, 3-phase, 4-wire wye transformer. Go to table 450.3(B) and select 125% primary only protection with secondary protection not required. But it IS required according to section 240.4 (F).
Shouldn't there be a note here in these tables stating this? Am I overlooking something?