I do not understand the question. Yes the primary is two phases of a 208/120 system, and the secondary will likely be 240 with a center tap. The center tap would be grounded (even if you dont need 120 for anything. Another option is to ground one "side" of the 240 resulting in one ungrounded conductor and one grounded conductor.120/208V Transformer is feeding 100A, 240V 1phase vessel at marina. They use 2 phases of conductor which is 208V plus or minus voltage drop while the vessel needs 240V.
What would that do to the transformer?
Sorry. The transformer size is 112.5 kva - primary 480v, secondary 120/208v.I do not understand the question. Yes the primary is two phases of a 208/120 system, and the secondary will likely be 240 with a center tap. The center tap would be grounded (even if you dont need 120 for anything. Another option is to ground one "side" of the 240 resulting in one ungrounded conductor and one grounded conductor.
Ah ok, so you have 208 serving the vessel that supposedly needs 240v? The transformer does not care. The loads on the vessel may or may not care. I would guess probably not an issue, but we would need more details of the loads and equipment to know for sure.Sorry. The transformer size is 112.5 kva - primary 480v, secondary 120/208v.
I see Thats why I can’t find much information I was just wondering if it damages the transformer. I dnt have detailed information about the loadsAh ok, so you have 208 serving the vessel that supposedly needs 240v? The transformer does not care. The loads on the vessel may or may not care. I would guess probably not an issue, but we would need more details of the loads and equipment to know for sure.
The transformer will not be damaged. It is likely (over 50%, less than 100%) sure that the vessel will operate at 208. If 240 __TWO WIRE__ is required, a boost transformer is the solution. If 120-0-120 is required, 2 boost transformers are the solution.I see Thats why I can’t find much information I was just wondering if it damages the transformer. I dnt have detailed information about the loads
Couldn't it also be done with a single transformer with a center tap grounded 240V secondary and two phases of the 208 with no neutral on the primary?If 120-0-120 is required, 2 boost transformers are the solution.
Two phases of the 208 is still 208V, not 240VCouldn't it also be done with a single transformer with a center tap grounded 240V secondary and two phases of the 208 with no neutral on the primary?
The vessel needs 240V with 2Hot+1N+1GThe transformer will not be damaged. It is likely (over 50%, less than 100%) sure that the vessel will operate at 208. If 240 __TWO WIRE__ is required, a boost transformer is the solution. If 120-0-120 is required, 2 boost transformers are the solution.
With no doubt, you need the vessel requirements.
That statement requires further detail, as has already been commented. The vessel was obviously designed for 120/240V. But if all the loads are 120V, then it doesn't need 120/240V, it will run fine on 120/208V. If there are 240V 2-wire loads, then each one can be evaluated to determine if it really needs 240V, or would work fine on 208V. Likewise if there are 120/240V 3-wire loads.The vessel needs 240V with 2Hot+1N+1G
If 240 __TWO WIRE__ is required, a boost transformer is the solution. If 120-0-120 is required, 2 boost transformers are the solution.
That makes sense. I’m waiting for the information, the reason I opened the thread was to know if it has been damaging the transformerThat statement requires further detail, as has already been commented. The vessel was obviously designed for 120/240V. But if all the loads are 120V, then it doesn't need 120/240V, it will run fine on 120/208V. If there are 240V 2-wire loads, then each one can be evaluated to determine if it really needs 240V, or would work fine on 208V. Likewise if there are 120/240V 3-wire loads.
Cheers, Wayne
Well since you mentioned it is a 112.5kVA transformer and that you are only supplying something with two lines and the neutral that something can only be 75kVA maximum, you don't have the remaining 37.5 kVA of the unused phase available for utilization here. Proper overcurrent protection should open circuit if overloaded though.That makes sense. I’m waiting for the information, the reason I opened the thread was to know if it has been damaging the transformer
Yes. That is the best way.Couldn't it also be done with a single transformer with a center tap grounded 240V secondary and two phases of the 208 with no neutral on the primary?
They wouldn't. 120 volt loads would be supplied directly from the utility; no change. And the boost (auto)transformer(s) would supply only the 240-volt loads.It's not clear to me how 2 boost transformers could be used to produce 120-0-120 (i.e., with the two 120V phases 180 degrees apart) when being provided with 120/208V.
That would not be a buck-boost application but rather a separately derived system and will need to be full kVA rated and not just rated for the amount of boost like an autotransformer would be.Couldn't it also be done with a single transformer with a center tap grounded 240V secondary and two phases of the 208 with no neutral on the primary?
Um, OK, on the primary side of the transformer, but what about on the secondary side? I am proposing a 208V ungrounded primary to 240V center tapped, grounded secondary transformer. I know that, for example, a 208V delta to 480/277V wye with a grounded neutral works; this seems similar to me.Two phases of the 208 is still 208V, not 240V
But it would work, right? My question was theoretical, not necessarily practical.That would not be a buck-boost application but rather a separately derived system and will need to be full kVA rated and not just rated for the amount of boost like an autotransformer would be.
Yes.But it would work, right? My question was theoretical, not necessarily practical.