Hey Guys,
I had a call to me today from someone asking me a question on a specific transformer setup and I told him to install ground detectors but i made me think ...and I figured you all may have some additional info.
1.) He has a 27 KVA step up transformer which has 208V primary Wye and a 480V secondary Delta config.
2.) The secondary conductors are leaving the transformer and feeding an elevator control panel.....he has only run (3) conductors for the 480V naturally as well as an EGC.
He informed me he did connect to the water pipe ground from the transformer and to the case of the transformer....
He has a primary overcurrent device ( fuses ) and has a grounded conductor run to the OCPD...but then into the transformer no grounded conductor as it is not needed in his setup.
My question is ( and I told him to install ground detectors )...he wanted to make sure that the fuses would blow and protect the transformer...he asked if he should install a system bonding jumper connection from the HO in the transformer ( thats right..no XO exists ) and the case and I said no.
Any suggestions on this......would anyone have additional info to add.
I had a call to me today from someone asking me a question on a specific transformer setup and I told him to install ground detectors but i made me think ...and I figured you all may have some additional info.
1.) He has a 27 KVA step up transformer which has 208V primary Wye and a 480V secondary Delta config.
2.) The secondary conductors are leaving the transformer and feeding an elevator control panel.....he has only run (3) conductors for the 480V naturally as well as an EGC.
He informed me he did connect to the water pipe ground from the transformer and to the case of the transformer....
He has a primary overcurrent device ( fuses ) and has a grounded conductor run to the OCPD...but then into the transformer no grounded conductor as it is not needed in his setup.
My question is ( and I told him to install ground detectors )...he wanted to make sure that the fuses would blow and protect the transformer...he asked if he should install a system bonding jumper connection from the HO in the transformer ( thats right..no XO exists ) and the case and I said no.
Any suggestions on this......would anyone have additional info to add.