dduffee260
Senior Member
- Location
- Texas
We have a building that was previously 240/120 3 phase. We upgraded the service to a 208/120 wye system. The engineer called for a 208 delta to 240 wye transformer to be installed. Square D does not make a 208 delta to 240 wye transformer that I can see. If we simply run the neutral from the 208 switchboard to the 240 panel what is the issue? The lighting loads are the only neutral loads on the smaller panel. They total about 30 amps on an 800 amp panel. Does anyone see a problem with simply carrying the neutral wire thru the transformer to the 800 amp panel?