M mitch cochrell Member Nov 9, 2009 #1 I have a couple of machines I have to provide power to. They are both 480v 3 phase. I only have 120v/240v high leg service. What type of transformer do I need to make this work?
I have a couple of machines I have to provide power to. They are both 480v 3 phase. I only have 120v/240v high leg service. What type of transformer do I need to make this work?
Pierre C Belarge Senior Member Location Westchester County, New York Nov 9, 2009 #2 A delta/wye transformer sized to the loads. Possibly larger if you think there is the possibility of additional loads later.
A delta/wye transformer sized to the loads. Possibly larger if you think there is the possibility of additional loads later.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Nov 9, 2009 #3 Pierre C Belarge said: A delta/wye transformer sized to the loads. Click to expand... Would not a D-D also work?
Pierre C Belarge said: A delta/wye transformer sized to the loads. Click to expand... Would not a D-D also work?
W wireguru Senior Member Nov 10, 2009 #4 is the service open delta or do you have real 3ph high leg? Are you adding alot of load the poco doesnt know about?
is the service open delta or do you have real 3ph high leg? Are you adding alot of load the poco doesnt know about?