Transformer Question

Status
Not open for further replies.
I have a machine that runs on 480 volts only and my incoming power is 240 3 phase delta with a stinger leg. I have a transformer that is delta primary and wye secondary. I would like to know if this will work connecting the 240 volt delta to the wye secondary or if I need a transformer with a delta secondary and delta primary. This transformer's secondary is 200 volts and has multiple taps on the primary side from 240 to 480 volts.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The delta/wye is not a problem (you would ignore the neutral), however, I thing you would be ill advised to connect the 200 volt rated secondary to your 240 volt system.
 