Can somebody help me with a transformer question? I have a 3 phase 250 KVA 13200 Y - 120/240 delta tx. When I try a 2VM ratio test I inject 240vac on the secondary and read (pp) 12400 A/B, 8460 B/C, and 12400 A/C. the nameplate is a bit old and I suspect there is some crucial information I am missing. Could this be "T" connected? Do i need some factor (i.e 1.73,etc)when going from y to delta? Can i "backfeed" without ramifications? My question is, Can anyone help explain these values to me?