Hello All,
First of all this isn't my area of expertise and I am unfortunately stuck with providing a solution. Any thoughts or comments are greatly appreciated.
I have been tasked with providing a standalone transformer with primary breaker and enclosure to provide 400V directly to the equipment breaker . This transformer is intended to be placed next to the equipment but can be up to 25FT away. I was asked to also provide the cable connection between the transformer and the equipment breaker.
My Questions:
1. Since this transformer (Wye-Wye Autotransformer) does not meet NEC 240.4(F) requirements it must have secondary protection. Correct?
2. Is a secondary breaker required in the transformer enclosure? Or can Equipment breaker be considered the secondary? There will be approx. 25Ft of cable between the transformer enclosure and equipment breaker.
3. Any NEC requirements that prevent the use of flexible conduit or Portable cable between the transformer and equipment? I haven't found any yet and I don't have the capability to provide rigid conduit unless the customer does it themselves.
I have attached a google drive link to an image of my planning document for anyone who would like some of the details.
Google drive Image
Thank You for your time!
First of all this isn't my area of expertise and I am unfortunately stuck with providing a solution. Any thoughts or comments are greatly appreciated.
I have been tasked with providing a standalone transformer with primary breaker and enclosure to provide 400V directly to the equipment breaker . This transformer is intended to be placed next to the equipment but can be up to 25FT away. I was asked to also provide the cable connection between the transformer and the equipment breaker.
My Questions:
1. Since this transformer (Wye-Wye Autotransformer) does not meet NEC 240.4(F) requirements it must have secondary protection. Correct?
2. Is a secondary breaker required in the transformer enclosure? Or can Equipment breaker be considered the secondary? There will be approx. 25Ft of cable between the transformer enclosure and equipment breaker.
3. Any NEC requirements that prevent the use of flexible conduit or Portable cable between the transformer and equipment? I haven't found any yet and I don't have the capability to provide rigid conduit unless the customer does it themselves.
I have attached a google drive link to an image of my planning document for anyone who would like some of the details.
Google drive Image
Thank You for your time!