Elect117
- California
- Engineer E.E. P.E.
I got sent prints to review and the designer is planning on feeding two panelboards off of one dry type.
150kVA (480-208/120 3PH)
250kcmil to 250 MCB
600kcmil to 400A MCB
I already noted that the secondary protection didn't meet Table 450.3(B) Note 2.
But I didn't know if I needed to also mark the SBJ or GEC size for correction either. They have the SBJ and GEC sized at 1/0.
My questions is, should they have sized the SBJ and GEC as 600kcmil + 250kcmil = 850kcmil => 2/0 or is it based on the largest single conductor from the transformer (600kcmil => 1/0)?
If they needed 2/0, could you help point me to the section? Is it the "parallel" language that I am not interpretating right? I always thought parallel meant they started and ended at the same point like from chapter 310. The max current would be based on the largest conductor but do you need to consider them both faulting at the same time?
250kcmil to 250 MCB