dm9289
Industrial Maintenance Electrician
- Location
- Pennsylvania
- Occupation
- Industrial process repair/ maintenance Electrician
I see this situation often in the 3 very old factories I work and can use some clarification.
Transformer input 2 legs from a 480v system on a circuit breaker (primary protection).
Output 120/240v to feed a panel board main lug.
I believe the secondary conductors should be protected either by a disconnect or a panel main breaker based on info in 240.21(C)
Am I reading this correctly?
Only time no secondary protection is required seems to be for single voltage output if i am correct for example a 120 to 24 volt transformer
Thanks as always for straightening me out
Dave
Transformer input 2 legs from a 480v system on a circuit breaker (primary protection).
Output 120/240v to feed a panel board main lug.
I believe the secondary conductors should be protected either by a disconnect or a panel main breaker based on info in 240.21(C)
Am I reading this correctly?
Only time no secondary protection is required seems to be for single voltage output if i am correct for example a 120 to 24 volt transformer
Thanks as always for straightening me out
Dave