Here is the setup....all equipment is in one room...an open storage room. Clearances are not an issue...
MDP - 80A 3PH 480V cb feeds a 75kVa 480-120/208V transformer. Length of run is approximately 12 feet.
transformer feeds a 225A MLO panel. Run is 6' from transformer to lugs. Wire is 3/0.
The 225A panel feeds a UPS through a 100A 2P cb. Additional circuits out of here are 2- 2P 40A to feed air handlers in the UPS, 2- 3P 15A to feed A/C condensers for the UPS, 2- 1P 20A to feed other equipment for the UPS...so for those keeping score, that's 7 means of disconnect in this panel.
now the question - is a MCB required in the 225A panel?
MDP - 80A 3PH 480V cb feeds a 75kVa 480-120/208V transformer. Length of run is approximately 12 feet.
transformer feeds a 225A MLO panel. Run is 6' from transformer to lugs. Wire is 3/0.
The 225A panel feeds a UPS through a 100A 2P cb. Additional circuits out of here are 2- 2P 40A to feed air handlers in the UPS, 2- 3P 15A to feed A/C condensers for the UPS, 2- 1P 20A to feed other equipment for the UPS...so for those keeping score, that's 7 means of disconnect in this panel.
now the question - is a MCB required in the 225A panel?