Folks,
I am looking for your help to solve this problem.
I have a 30 kVA 480/208-120 V lighting transformer with a 50 A primary OCPD. The secondary of the transformer is terminated in a lighting panel with an incoming breaker of 220 A. The actual lighting load is not more than 10 kW.
Everything is outdoor.
What is the minimum size of the cable between transformer secondary and lighting panel?
The transformer and lighting panel are next to each other.
I am not sure if I have to size it based on the actual load (#8) or based on 225 A (breaker size of lighting panel) (3/0) or 50A (primary OCPD) (#1).
Please support your replays with NEC article number.
I am looking for your help to solve this problem.
I have a 30 kVA 480/208-120 V lighting transformer with a 50 A primary OCPD. The secondary of the transformer is terminated in a lighting panel with an incoming breaker of 220 A. The actual lighting load is not more than 10 kW.
Everything is outdoor.
What is the minimum size of the cable between transformer secondary and lighting panel?
The transformer and lighting panel are next to each other.
I am not sure if I have to size it based on the actual load (#8) or based on 225 A (breaker size of lighting panel) (3/0) or 50A (primary OCPD) (#1).
Please support your replays with NEC article number.