I have argued about this before. Do we have to derate the secondary conductors of a 4 wire 208/120Y transformer to 80%, based on having 4 current carring conductors in a raceway? Is the neutral conductor in this case current carring? (no harmonic loads also)
I am siding on no becuase of 310.15(B)4......a neutral conductor that carries only the unbalanced current from the other conductors "of the same circuit" shall not be required to be counted when applying the provisions of 310.15(B)(2)(a)....
Thanks
I am siding on no becuase of 310.15(B)4......a neutral conductor that carries only the unbalanced current from the other conductors "of the same circuit" shall not be required to be counted when applying the provisions of 310.15(B)(2)(a)....
Thanks