Sparky2791
Senior Member
- Location
- Northeast, PA
- Occupation
- Electrical Design
Hello –
Submitted this drawing for third party review to obtain a permit. Plan reviewer sent back this comment.
#1 It appears there is no secondary protection for Transformers T12 & T13 per 240.4(f) and 240.21(c).
#2 Once the OCPD is determined for above, please be sure all conductors are in compliance with 310.15.
I assume it is because we did not show that the panels had a main circuit breaker. (the red text was added for the purpose of this post). Does anyone else see any NEC issue with this. Agree with my assumption?
Thanks for looking!