Been having a debate with a coworker.
We are currently drawing up a plan to have a 75kva 3PH 480v Delta to 3PH 208/120Y transformer installed to feed a 3PH 208/120Y 42 circuit lighting and appliance panel.
We will have a 3PH 480v fused disconnect installed next to the transformer for the primary feed. The Secondary panel will be installed next to the transformer allowing for the secondary conductors to be no more than 10' in length.
Our debate is, I say that the secondary panel requires a main breaker to be installed to protect the secondary conductors. He says the primary disconnect will be sufficient to protect both the primary and secondary. I keep referencing NEC OCP "Tap rule" articles and he keeps referencing Transformer articles.
What are your thoughts and what NEC articles may we reference to finally get the right answer?
Thanks
We are currently drawing up a plan to have a 75kva 3PH 480v Delta to 3PH 208/120Y transformer installed to feed a 3PH 208/120Y 42 circuit lighting and appliance panel.
We will have a 3PH 480v fused disconnect installed next to the transformer for the primary feed. The Secondary panel will be installed next to the transformer allowing for the secondary conductors to be no more than 10' in length.
Our debate is, I say that the secondary panel requires a main breaker to be installed to protect the secondary conductors. He says the primary disconnect will be sufficient to protect both the primary and secondary. I keep referencing NEC OCP "Tap rule" articles and he keeps referencing Transformer articles.