Grouch1980
Senior Member
- Location
- New York, NY
HI all,
Say I have a transformer with a 250% maximum rated primary OCPD, and a 125% rated (or next size up) secondary OCPD based on table 450.3(B); my voltages are below 600 volts. The 125% rated OCPD takes care of protecting the transformer secondary.
Now I have to protect the secondary conductors. I look at 240.21(C)(1)... if my transformer is delta delta, then my secondary conductors are protected by the primary OCPD.
What now dictates the location of my 125% rated OCPD on the transformer secondary? Can it be 10 feet away, or 25 feet away?