Struggling to completely understand the bounding and grounding around transformer and sizing of neutrals leaving the secondary. From what I understand in most real world scenarios the neutral conductor will be sized to the expected load or to the same size as the ungrounded conductors. All of that aside to abide by the NEC minimum requirements, the size requirements are found in table 250.102(c)(1)....
So in a single raceway with 3- 3/0 ungrounded conductors leaving a transformer, I would size my Neutral/grounded conductor in accordance with the table and be left with a #4 minimum size?
In that same raceway I would also have a #4 supply-side bonding jumper?
If so would this remain the same regardless of me terminating the system bonding jumper in the transformer enclosure or the secondary panel enclosure?
Thanks for any info.
So in a single raceway with 3- 3/0 ungrounded conductors leaving a transformer, I would size my Neutral/grounded conductor in accordance with the table and be left with a #4 minimum size?
In that same raceway I would also have a #4 supply-side bonding jumper?
If so would this remain the same regardless of me terminating the system bonding jumper in the transformer enclosure or the secondary panel enclosure?
Thanks for any info.