Below is my understanding of a Transformer?s Secondary Currents, I?d like to confirm these assumptions are correct. Any comments?
I have a 480V : 240V/120V Single Phase transformer. The Primary is fed with 2 legs of a 480V supply, the Secondary (X1, X2, X3, X4) has X4 GND/NEU, X2-X3= 120V, X1= 240V.
The available secondary currents:
? 240V @ 41.7Amps
? 120V @ 41.7Amps (this is 41.7 not 83.3 since the 120V is a Center Tap effectively at 5KVA)
The available current to either output 120V or 240V is affected by the other?s current. For example; the 120V output is drawing 15Amps, therefore the current available at the 240V output will be 41.7A ? 15A = 26.7A. The same would be true for the 120V output; 240V output is at 20Amps, therefore the available current at the 120V output would be 41.7A - 20A = 21.7A.
I have a 480V : 240V/120V Single Phase transformer. The Primary is fed with 2 legs of a 480V supply, the Secondary (X1, X2, X3, X4) has X4 GND/NEU, X2-X3= 120V, X1= 240V.
The available secondary currents:
? 240V @ 41.7Amps
? 120V @ 41.7Amps (this is 41.7 not 83.3 since the 120V is a Center Tap effectively at 5KVA)
The available current to either output 120V or 240V is affected by the other?s current. For example; the 120V output is drawing 15Amps, therefore the current available at the 240V output will be 41.7A ? 15A = 26.7A. The same would be true for the 120V output; 240V output is at 20Amps, therefore the available current at the 120V output would be 41.7A - 20A = 21.7A.