I have a 1500kVA 4.16kV to 480V Delta-Wye transformer. I have calculated the secondary full load current of this transformer to be 1806A.
The secondary of this transformer is feeding a 2000A bus on a 480V MCC. The breaker (Siemens RL) on the secondary of this transformer feeding the MCC bus is set to 2000A. In reviewing this it appears that the transformer secondary breaker is set to feed a 2000A bus when the avaliable full load on the secondary is only capable of 1806A. This arrangement would appear to exceed the avaliable current from the secondary of the transformer and possibly cause damage if MCC bus is fully loaded.
Does this arrangement appear to be correct? Is there a particular NEC article that I can cite when I bring up this topic to the engineers?
I am reviewing a power systems study for the first time, which is the reason for alot of posts recently. I appreciate the help and responses that people have been providing. This is a GREAT Forumn!!!
The secondary of this transformer is feeding a 2000A bus on a 480V MCC. The breaker (Siemens RL) on the secondary of this transformer feeding the MCC bus is set to 2000A. In reviewing this it appears that the transformer secondary breaker is set to feed a 2000A bus when the avaliable full load on the secondary is only capable of 1806A. This arrangement would appear to exceed the avaliable current from the secondary of the transformer and possibly cause damage if MCC bus is fully loaded.
Does this arrangement appear to be correct? Is there a particular NEC article that I can cite when I bring up this topic to the engineers?
I am reviewing a power systems study for the first time, which is the reason for alot of posts recently. I appreciate the help and responses that people have been providing. This is a GREAT Forumn!!!