We have a 480-120/208 transformer located on a mezzanine that has no permanent access ladder. The primary overcurrent fuse size is 250a. The secondary conductors consist of (2) sets of 4, 250kcml cu thhn conductors. If the secondary overcurrent device is a 600amp circuit breaker in a panelboard and the conductors are in conduit, does this meet the requirements of 240.21.C.6,for the conductors to be up to 25' in lenght? If not what would be required to make this comply? I know if I install an overcurrent device at the transformer on the mezzanine (to stay within the 10') it would not be considered "readily accessible".