sevlander
Member
- Location
- new jersey
What is the maximun overcurrent protection allowed an the secondary of a 45KVA 480-120/208V 3PH transformer? I believe it is 125A , but a plan we are bidding is calling to replace the existing 100A 120/208 panel with a 150A MCB panel using the existing transformer. The transformer secondary amps are listed as 125, how can this be allowed at 150A? Is the MOCP 125% of the 125A nameplate? I was always taught that this nameplate amperage is already at max and the 125% cannot be used. Please advise where it is shown in NEC if I am wrong. Thanks