Hello all, I have been reading this forum for a while, but this is my first time posting! I am working on selecting the appropriate electrical equipment & panels for a project I am working on and had a question about transformer secondary OCPD. All of this equipment will be in the same room (inside of a shipping container).
Main Panel
-------------------
800A 480V Main Breaker fed by POCO
-400A breaker feeding 300 kva transformer
-300A breaker feeding 200 kva transformer
-300A breaker feeding second 200 kva transformer
300kva 416/240 transformer
-------------------
Option 1: Feed main lug panel with (4) 150A breakers (125% of the transformer secondary is only 520A so not sure if this is code compliant)?
Option 2: Feed 500A main breaker panel with (4) 150A breakers
Option 3: Feed (4) 150A fused disconnects directly from the transformer secondary instead of having a panel. (Is this code compliant?)
The 150A disconnects/breakers feed PDUs for computer equipment.
200kva 416/240 transformer (typical for both)
-------------------
Option 1: Feed main lug panel with (2) 150A breakers (I think this is code compliant because 125% of the transformer secondary is 347A)
Option 2: Feed 250A or 300A main breaker panel with (2) 150A breakers
Option 3: Feed (2) 150A fused disconnects directly from the transformer secondary instead of having a panel. (Is this code compliant?)
The 150A disconnects/breakers feed PDUs for computer equipment.
I was wondering if y'all might know if the above options are NEC compliant when it comes to secondary protection of the transformer. Thanks for your input or suggestions!
Matt
Main Panel
-------------------
800A 480V Main Breaker fed by POCO
-400A breaker feeding 300 kva transformer
-300A breaker feeding 200 kva transformer
-300A breaker feeding second 200 kva transformer
300kva 416/240 transformer
-------------------
Option 1: Feed main lug panel with (4) 150A breakers (125% of the transformer secondary is only 520A so not sure if this is code compliant)?
Option 2: Feed 500A main breaker panel with (4) 150A breakers
Option 3: Feed (4) 150A fused disconnects directly from the transformer secondary instead of having a panel. (Is this code compliant?)
The 150A disconnects/breakers feed PDUs for computer equipment.
200kva 416/240 transformer (typical for both)
-------------------
Option 1: Feed main lug panel with (2) 150A breakers (I think this is code compliant because 125% of the transformer secondary is 347A)
Option 2: Feed 250A or 300A main breaker panel with (2) 150A breakers
Option 3: Feed (2) 150A fused disconnects directly from the transformer secondary instead of having a panel. (Is this code compliant?)
The 150A disconnects/breakers feed PDUs for computer equipment.
I was wondering if y'all might know if the above options are NEC compliant when it comes to secondary protection of the transformer. Thanks for your input or suggestions!
Matt