150KVA, 208/120Y three phase transformer has parallel secondary conductors at 3/0 landing in a 400amp breaker. According to the code calculation 150,000/(208x1.732)=416.4.
Table 450.3(B) 125% (Currents of 9 amperes or more Primary and secondary protection)
1.25x416.4=520.5
Table 450.3(B) Note 1 one allows next size up standard rating.
Table 240.6(A) Next size up from 520 would be 600 or I can go down to 500 standard rating. Sticking with the 500 standard rating I divide by two 500/2=250 (parallel run)
Table 310.16-75 degree column 255 requires 250 kcmil.
What am I missing here? How come this print has the secondary conductors protected by a 400amp breaker? This is a service for two-Level 2 electrical vehicle charging stations which are considered continuous loads. The only thing I can think of is an exception to the 125% where the secondary conductors are allowed to be protected at 100% of the current rating (416.4A) which would then make sense moving down to a 400amp main breaker. The problem is I can't find any exception in regards to transformers or EVSI equipment that allows this.
Table 450.3(B) 125% (Currents of 9 amperes or more Primary and secondary protection)
1.25x416.4=520.5
Table 450.3(B) Note 1 one allows next size up standard rating.
Table 240.6(A) Next size up from 520 would be 600 or I can go down to 500 standard rating. Sticking with the 500 standard rating I divide by two 500/2=250 (parallel run)
Table 310.16-75 degree column 255 requires 250 kcmil.
What am I missing here? How come this print has the secondary conductors protected by a 400amp breaker? This is a service for two-Level 2 electrical vehicle charging stations which are considered continuous loads. The only thing I can think of is an exception to the 125% where the secondary conductors are allowed to be protected at 100% of the current rating (416.4A) which would then make sense moving down to a 400amp main breaker. The problem is I can't find any exception in regards to transformers or EVSI equipment that allows this.