I have would like to install a 225 Amp panel board thirty feet away from the transformer that is supplying it. I have primary OCPD protection on the transformer. Does the NEC require extra protection other than the main OCPD in this panel board?
If it is single phase or 3-wire delta-to 3-wire delta, then the primary OCPD will protect the secondary conductors proportional to its ampacity scaled by the voltage ratio, without any secondary OCPD. For instance, consider a 100A primary OCPD on a 240-to-120 single phase transformer. As long as the secondary conductors are at least rated for 200A, they do not need secondary OCPD.
The idea of the above, is that for simple configurations where faults will line up winding-to-winding, a fault will stay on the same phase across the transformer, and not go undetected because it will not get distributed across multiple primary phases.
This doesn't happen, if you have any transformer with a WYE system or a 4-wire delta system on either side. It will require OCPD on the secondary as well. In these cases, secondary fault currents can distribute across multiple phases of the primary, and go undetected.
240.21(C) gives us the rules for how far transformer secondary conductors can extend, when OCPD is required. And what sizing requirements they have. Indoors, it is limited to 10 ft or 25 ft, depending on what proportion of the total available KVA the conductors will be sized to meet.