is the transformer secondary overcurrent protective device required to be located in or on the transformer enclosure?
 
No, there is no such requirement.

It is very common for a MCB in a panelboard to servce as the transformer secondary overcurrent protection.
 
is the transformer secondary overcurrent protective device required to be located in or on the transformer enclosure?
No.
See 240.21(C) for protection of transformer secondary conductors.
Most installations seem to fall within 10' and 25' limits.
 