But you can't really use a transformer with no conductors. 240.4(F) tells you that you need secondary protection.I'm confused. We are talkin about the transformer itself here not the conductors right? I don't see any restrictions with primary only protection as long as we comply with the ocpd percentages given in 450.3 (b). What is 450.30 (a) I don't have that in my 2011 (job site beater codebook), was there a change?
If we are talking under 1000 volts primary, it's designers choice... really [Table 450.3(B)].I don't do much transformer installations. Why would one provide primary AND secondary protection on 3phase transformer VS just primary only?
Thanks
The primary is 240V and secondary is 480V with a 45KVA transformer. Is the primary fuse required on the primary side?
Thanks
Where else would you put the primary fuse(s)? :slaphead:... Is the primary fuse required on the primary side?
Where else would you put the primary fuse(s)? :slaphead: A transformer always requires, at the very least, primary OCPD (on the primary side :lol.
PS: If you are back feeding a transformer with a PV system, for example, you are required to evaluate OCP both ways, i.e. each side as a primary [705.30(B)].
Analyzing each side as primary for primary OCP is a requirement. The whole point is that neither side is oversized. Neither side can exceed 125% of the transformer rated current. This is for nominal operation, not a fault condition.Wouldn't that only be true if the export capacity is physically able to break the transformer or conductor limits? It's possible if there's a short on the utility side and there's 9,000 lbs of rotating mass in a large mechanical inverter but there's practically no energy stored in the static converter and none in the panel.