MechEdetour
- NY, USA
- Design Engineer
In this Mike Holt transformer install example, it is determined that a 175A overcurrent device is required for the secondary based on:
It seems though it is assumed the continuous load in this install will use the transformer to it's full capacity, so full load current on secondary was multiplied by 1.25 to determine overcurrent protection. But if the transformer is oversized, and say continuous loads will not exceed say 120A, then a panel with a 150A main (it will serve as the transformer secondary protection) is ok right?
https://www.mikeholt.com/mojonewsarchive/NEC-HTML/HTML/TransformerInstallation~20020516.htm
Overcurrent Protection Device Size: Where a feeder supplies continuous loads, the rating of the (secondary) overcurrent device shall not be less than 125 percent of the continuous load [215.3] as listed in 240.6(A).
45 kVA 125A x 1.25 = 156A, 175A protection