GarrettGalyen
Member
- Location
- San Jose, CA
I came up with an issue with an inspector. The Inspector is stuck on NEC 240.4(F) Which states that transformers that are not delta-delta or single phase are NOT considered to be protected by primary OCP.
But, According to NEC 240.24 {C}2 Primary OCP is permitted. And it doesn't matter what type of transformer it is.
This is also reinforced by 450.3 and table 450.3(B).
I have a 480V board with a MCB that is feeding a transformer (delta-wye) via ocp. The transformer is feeding a 208V board within 10' routing distance.
Does there need to be OCP on the secondary side?
But, According to NEC 240.24 {C}2 Primary OCP is permitted. And it doesn't matter what type of transformer it is.
This is also reinforced by 450.3 and table 450.3(B).
I have a 480V board with a MCB that is feeding a transformer (delta-wye) via ocp. The transformer is feeding a 208V board within 10' routing distance.
Does there need to be OCP on the secondary side?