transformer secondary protection
benmin
Maine
Master Electrician
480/277 to 208/120 45kva transformer. Primary protected by 70A breaker. Secondary is under 10' long supplying a panel. Can the panel be Main lug or does it need to be a main breaker?
The transformer doesn't care. However the panelboard will require a main device, somewhere between it and the transformer (408.36).
Ahh I see it now. 408.36 sends you to 240.21(c)(1) in this case. I was eying 240.21(c)(2) and should have noticed the informational note. Thanks