I have a 3 phase 112.5 kva 480-208/120 transformer being protected by a 200A primary breaker where the secondary is being tapped into 3 single phase 208V/120 panels each being protected by 200A fused disconnects. Looking at table 450.3(B) note 2, in order for this to be considered secondary protection, the sum of all OCPD's must not exceed 125% of 312A.
Since these are 3 single phase 208/120 circuits, do they collectively provide 200A of protection as a 3 phase fused disconnect would?