timm333
Senior Member
- Location
- Minneapolis, MN
- Occupation
- Electrical Design Engineer
I am trying to figure out the NEC rules for the protection and sizing of transformer secondary cable in supervised location. The transformer is 500kVA 4160V-480V/277V (delta-wye grounded). The length of the transformer secondary cable is 100 feet. NEC table 450.3(A) states that the secondary protection is not required in the supervised location. However, NEC 240.21(C)(3) states that if the secondary protection is not provided, then the length of the transformer secondary cable cannot be more than 25 feet.
This transformer feeds a 480V switchboard which has a 400A main breaker. This 400A breaker is on the secondary side of transformer, but it is 100 feet away from the transformer. Can this 400A main breaker of switchboard be used as the secondary protection of the transformer? Thanks
This transformer feeds a 480V switchboard which has a 400A main breaker. This 400A breaker is on the secondary side of transformer, but it is 100 feet away from the transformer. Can this 400A main breaker of switchboard be used as the secondary protection of the transformer? Thanks