Transformer secondary protection

Status
Not open for further replies.

Jeff@BTE

New User
Location
Maryland
Occupation
Estimator
When protecting the secondary output for a 120/208v 3 phase Y transformer, is there a maximum length of unprotected wire before going from the output of the transformer to the main breaker of the electrical panel or fused disconnect?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The maximum length is unlimited IF you meet the requirements of 240.21(C)(4) {2017} but the length can be limited depending on which of the 240.21(C) tap rules is applicable + other rules in 240 Part VIII for supervised industrial applications.,
 