When protecting the secondary output for a 120/208v 3 phase Y transformer, is there a maximum length of unprotected wire before going from the output of the transformer to the main breaker of the electrical panel or fused disconnect?
The maximum length is unlimited IF you meet the requirements of 240.21(C)(4) {2017} but the length can be limited depending on which of the 240.21(C) tap rules is applicable + other rules in 240 Part VIII for supervised industrial applications.,