I came across a 150kVA 480V Delta primary / 208V wye seconary 3-phase transformer the other day. The primary was proteced by a 150A fused switch which is not adequate for the primary full load capacity of the transformer however my focus here is more on the secondary of the transformer.
The secondary cables from the transformer are 600MCM and feed a 208V switchboard with no main protective device. There are six fused switches in this switchboard whose vaules add up to more than 600A. Note 2 of table 450.3(B) allows for the transformer to not have a secondary protective device if it terminates somewhere where there are not more than 6 protective devices in one location that do not add up to more than 125% of transformer secondary full load. With the secondary full load of this transformer being 416A, 125% or this value would be 521A and therefore the fact that the six protective devices in this switchboard add up to more than 600A is a violation. Would you agree? Would you also agree that a main breaker needs to be added into this switchboard?
In additional to this tapped off the main bus in the switchboard with no protective device is a set of 400MCM cables which is tapped to feed two panelboards about 5ft away. The tap off of this 400mcm cable is made in a trough and the tap conductors to the panels are 4/0 each. Each panel has a 225A main breaker. To me this just further violates the secondary protection exception for 3 reasons being that it now adds more than six breakers that the transformer terminates into, these breakers are all not in one loction (5ft away in different equipment) and the additional breaker size only increases the combined value of protective devices.
So in summary I see three problems here why the transformer secondary is not adequately protected:
1) Protective devices are all not in one location
2) There are more than six protective devices that the secondary of the transformer terminates into
3) Combined value of protective devices is over 125% of transformer secondary current.
Would you guys agree with all of this?
Also how would the tapped conductor off of the switchboard to the panelboards be viewed. Wouldn't his be a tap violation as well?
The secondary cables from the transformer are 600MCM and feed a 208V switchboard with no main protective device. There are six fused switches in this switchboard whose vaules add up to more than 600A. Note 2 of table 450.3(B) allows for the transformer to not have a secondary protective device if it terminates somewhere where there are not more than 6 protective devices in one location that do not add up to more than 125% of transformer secondary full load. With the secondary full load of this transformer being 416A, 125% or this value would be 521A and therefore the fact that the six protective devices in this switchboard add up to more than 600A is a violation. Would you agree? Would you also agree that a main breaker needs to be added into this switchboard?
In additional to this tapped off the main bus in the switchboard with no protective device is a set of 400MCM cables which is tapped to feed two panelboards about 5ft away. The tap off of this 400mcm cable is made in a trough and the tap conductors to the panels are 4/0 each. Each panel has a 225A main breaker. To me this just further violates the secondary protection exception for 3 reasons being that it now adds more than six breakers that the transformer terminates into, these breakers are all not in one loction (5ft away in different equipment) and the additional breaker size only increases the combined value of protective devices.
So in summary I see three problems here why the transformer secondary is not adequately protected:
1) Protective devices are all not in one location
2) There are more than six protective devices that the secondary of the transformer terminates into
3) Combined value of protective devices is over 125% of transformer secondary current.
Would you guys agree with all of this?
Also how would the tapped conductor off of the switchboard to the panelboards be viewed. Wouldn't his be a tap violation as well?