Table 430.3 (B)
Secondary Protection
Currents of 9 amps or more
(second row)125% (see Note 1)
Note 1 allows "next higher standard rating shall be permitted." for fuse or breaker.
240.21(C) "The provisions of 240.4(B) shall not be permitted for transformer secondary conductors."
240.4(B) being next higher device shall be permitted.
I am confused at how 430.3(B) allows next size up for secondary OCPD, and 240.21(C) does not allow next size up OCPD.