Hello all,
I am working on a new mixed use residential/commercial building where we have a 1200A switchgear being fed from a 750KVA transformer. Now we are having issues with lead times for the switchgear that go from 6months to over a year. I have been tasked with finding a cost effective solution and I have a couple of ideas that I would love to run by you guys.
1- Provide double lugs on the secondary side of the transformer and feed (2)600A MCB distribution panels. I'll need to put the panels within 10FT of the transformer or provide redundant fused disconnects within 10 feet of the transformer and run the feeder to my two panels 20+ feet away. The 600A distribution panel parts are in stock and only have lead times of 6-12weeks. Looking through the NEC this looks code compliant to me, but I am trying to figure out of I need to be withing 10FT of the transformer on the secondary side.
2- Provide a 1200A disconnect within 10FT of the secondary side of the switch gear and feed a wire trough that I can tap as needed. The 1200A disconnect has a lead time of 8-16weeks. Each tap would have a MCB panel. This also looks code compliant to me.
Does anyone see anything wrong with these two solutions or have better recommendations?
I am working on a new mixed use residential/commercial building where we have a 1200A switchgear being fed from a 750KVA transformer. Now we are having issues with lead times for the switchgear that go from 6months to over a year. I have been tasked with finding a cost effective solution and I have a couple of ideas that I would love to run by you guys.
1- Provide double lugs on the secondary side of the transformer and feed (2)600A MCB distribution panels. I'll need to put the panels within 10FT of the transformer or provide redundant fused disconnects within 10 feet of the transformer and run the feeder to my two panels 20+ feet away. The 600A distribution panel parts are in stock and only have lead times of 6-12weeks. Looking through the NEC this looks code compliant to me, but I am trying to figure out of I need to be withing 10FT of the transformer on the secondary side.
2- Provide a 1200A disconnect within 10FT of the secondary side of the switch gear and feed a wire trough that I can tap as needed. The 1200A disconnect has a lead time of 8-16weeks. Each tap would have a MCB panel. This also looks code compliant to me.
Does anyone see anything wrong with these two solutions or have better recommendations?