What is the maximum distance for overcurrent protection for a underground feeder from the transformer secondary, located out side, to a main circuit breaker panel located inside.
Refer to 2002 NEC 240.21(C) for transformer secondary conductors. "Outside secondary of building or structure" are not distance limited when meeting the listed requirements.