Transformer secondary

Status
Not open for further replies.

pross

New member
What is the maximum distance for overcurrent protection for a underground feeder from the transformer secondary, located out side, to a main circuit breaker panel located inside.
 

nvcape

Senior Member
Re: Transformer secondary

Refer to 2002 NEC 240.21(C) for transformer secondary conductors. "Outside secondary of building or structure" are not distance limited when meeting the listed requirements.
 