Attached sketch shows 480V to 208V/120V three phase 150kva transformer secondary conductor 2 sets of 5#4/0 + 2/0 fed going into trough. The conductors are tapped to three panelboards P1, P2, P3as shown. Each tap is 4#1/0 + #2 GRD to each panelboard as shown in sketch. Each secondary panelboard has 250A MCB as shown in sketch. The transformer primary is fed from 300A breaker.
Questions:
1. Is the attached sketch code complaint in terms of secondary conductors being tapped as shown? If not then which code section. I don’t see can’t tap a tap NEC 2014 for transformer secondary conductor.
2. How would one size equipment grounding conductor from xfmr secondary conductor to trough and from trough to panelboard? Based off of what?