Transformer separation 450.27 n 28

Status
Not open for further replies.

Electriman

Senior Member
Location
TX
Greetings,

In order to meet this requirement what do you recommend when there is an oil filled transformer next to other equipment i.e. another transformer or a back up generator outdoor?

Thank you in advance.
 

ron

Senior Member
Is this an existing or new condition? If new, go with FR3 liquid that is not considered a fire hazard (we install them inside buildings).
If existing, concrete block walls often are good.
 