I have a 225 kVA 480:120/208 3-phase transformer located 100' from the Main Distribution Panel. The engineered plans have the transformer being fed from a 350A 3-pole 480V breaker with a 3-1/2" conduit with (3) 500 kcmil conductors and a #3 copper equipment ground. The transformer feeds a 600 amp 120/208V 3-phase distribution panel. The drawings call for a parallel set of 500 kcmil conductors from the secondary of the transformer to the distribution panel 600A main breaker. Based on these conductors, the drawings also call for a 2/0 copper to the water pipe, building steel and ground rod.
Here is my question, why can't I substitute the #3 copper equipment ground in the feeder conduit to the transformer with a 2/0 copper conductor? This would bond the transformer case and the XO terminal (grounded terminal) back to all of the building electrodes that have already been established at the MDP? the 2/0 is sized off of the secondary ungrounded service conductors of the transformer secondary and would provide an easy way to bond the seperately derived service. The copper water piping in the vicinity of the transformer are the same copper lines near the service as the office building isnt that large.
I appreciate any thoughts on this matter.
Thanks,
Mike
Here is my question, why can't I substitute the #3 copper equipment ground in the feeder conduit to the transformer with a 2/0 copper conductor? This would bond the transformer case and the XO terminal (grounded terminal) back to all of the building electrodes that have already been established at the MDP? the 2/0 is sized off of the secondary ungrounded service conductors of the transformer secondary and would provide an easy way to bond the seperately derived service. The copper water piping in the vicinity of the transformer are the same copper lines near the service as the office building isnt that large.
I appreciate any thoughts on this matter.
Thanks,
Mike