KSM8565
Member
- Location
- United States
I'm trying to calculate the size of a transformer. I would appreciate any and all input. I have 2#8's (THHN) available to use from existing panel (120/208V) to outside hand vault (will be in separate building). I need to feed a 3.3KW heater (208V 1PH), 6-120V fluorescent fixtures (1.5 amps), 1 general purpose receptacle and 1 exhaust fan (non-coincidental load to the heater). I figure a total of no more than 24 FLA at any given time. What's the smallest transformer I can install given that we could install a 2P/50 amp breaker (with 75 degree terminals) in the existing panel?