transformer size

Status
Not open for further replies.

daddy0

New member
have 3 ph 4wire 200amp 480/277v panel need 120 volt panel to feed 36 diesel heaters at 11 amps each. Came up with 100kva step down transformer feeding 2 200amp 120/208v panels. did i calculate correct?
 
Dad, welcome to the forum! :)

have 3 ph 4wire 200amp 480/277v panel need 120 volt panel to feed 36 diesel heaters at 11 amps each. Came up with 100kva step down transformer feeding 2 200amp 120/208v panels. did i calculate correct?
Let's see: 36 x 120 x 11 = 47,520. You're just under half of the transformer's capacity.

With 12 heaters per phase, your load would be 132a. You could use a single 200a panel.
 
Larry don't I have to multiply those heaters by 1.25 also? or are t-stats involved here?

NEC 424.3(B) state's that fixed electric space heating shall be considered continuous load. These are diesel heaters. What are they used for? NEC 427.4 say's the same for fixed electric heating equipment for pipelines and vessels.
 
Last edited:
You don't need to multiply the transformer by 1.25 The minimum transformer would be according to the first post, i.e. 47.52KVA. If you could show that the heaters will not be operating at the same time (running versus connected) then you might be able to prove a 45KVA is adequate. That is if you are trying to go cheapest first cost. Otherwise, if you bump up to 75KVA, then why not install full capability, as mentioned.

As far as the 1.25. The 1.25 factor should be applied to the equipment rating, not the load. The load is 47.52KVA, the load will never be 47.52KVA x 1.25. The breakers, cable, and panel need to be rated for 1.25 greater than the load, but not the transformer.
 