Let's see: 36 x 120 x 11 = 47,520. You're just under half of the transformer's capacity.have 3 ph 4wire 200amp 480/277v panel need 120 volt panel to feed 36 diesel heaters at 11 amps each. Came up with 100kva step down transformer feeding 2 200amp 120/208v panels. did i calculate correct?
Dad, welcome to the forum!
Let's see: 36 x 120 x 11 = 47,520. You're just under half of the transformer's capacity.
With 12 heaters per phase, your load would be 132a. You could use a single 200a panel.
I presumed the latter, but you could be right.Larry don't I have to multiply those heaters by 1.25 also? or are t-stats involved here?
Larry don't I have to multiply those heaters by 1.25 also? or are t-stats involved here?
Even so, I'd say our single-200a-panel idea is sound.
Larry don't I have to multiply those heaters by 1.25 also? or are t-stats involved here?