This question may sound stupid but i have looked and looked in the NEC book and I cannot find the Air conditioning rules in 220.
There is the lighting demand factor for office/banks in 220.40
There is the receptacles demand rules for office/banks in 220.44
There is the kitchen equipment for "Other than dwelling" banks/offfice in 220.56
BUT I cannot find anything about Air Conditioning for Office or banks.
Am i blind?? Looking in the wrong place????
Maybe you can help me.
Question:
This question is with respect to transformer sizing
Is there a VA/sq ft. factor for AC in office/ banks?
If we know the total connected AC nameplate loads for office spaces in a building do we just add all of them up and use it at 100%
I have a building with 8 small office spaces. Each has a 9 kva AC nameplate.
do i just multiply 9 kVA x 8 and use 72 kVA for transformer sizing purposes
Help on this matter is greatly appreciated.
There is the lighting demand factor for office/banks in 220.40
There is the receptacles demand rules for office/banks in 220.44
There is the kitchen equipment for "Other than dwelling" banks/offfice in 220.56
BUT I cannot find anything about Air Conditioning for Office or banks.
Am i blind?? Looking in the wrong place????
Maybe you can help me.
Question:
This question is with respect to transformer sizing
Is there a VA/sq ft. factor for AC in office/ banks?
If we know the total connected AC nameplate loads for office spaces in a building do we just add all of them up and use it at 100%
I have a building with 8 small office spaces. Each has a 9 kva AC nameplate.
do i just multiply 9 kVA x 8 and use 72 kVA for transformer sizing purposes
Help on this matter is greatly appreciated.